Is the actual room temperature maybe already below the goal temperature? Your scenario will just operate in the exact moment when the room temperature falls below goal temp.
You probably need to solve it like this:
IF
Change of Room Temperature happens
AND
Room Temperature is below Goal Temperature
THEN
Turn on valve
You then would need a second rule that turns it off again similar to the one above using 'Room Temperature is over Goal Temperature' as a condition.
IF
Change of Room Temperature happens
AND
Room Temperature is over Goal Temperature
THEN
Turn off valve
You probably need to solve it like this:
IF
Change of Room Temperature happens
AND
Room Temperature is below Goal Temperature
THEN
Turn on valve
You then would need a second rule that turns it off again similar to the one above using 'Room Temperature is over Goal Temperature' as a condition.
IF
Change of Room Temperature happens
AND
Room Temperature is over Goal Temperature
THEN
Turn off valve